Acknowledgments
6 Discussion and conclusion
The flow charts given in Figs 5.15 and 5.16 are for a bridge with the general layout shown in Fig. 5.1. Figure 5.15, for the superstructure, provides design forces and displacements for the beams and at the four sets of bearings shown. Figure 5.16, for the columns, takes account of system instability shown in Fig. 5.1(b). Instability of members in compression is covered in comments on clause 6.7.3.4.
For simplicity, the scope of these charts is limited by assumptions, as follows:
. Fatigue, vibration, and settlement are excluded.
. Axial force in the superstructure (e.g. from friction at bearings) is negligible.
. The main imposed loading is traffic Load Model 1, from EN 1991-2.
. Only persistent design situations are included.
. The limit states considered are ULS (STR) and SLS (deformation and crack width).
. The superstructure consists of several parallel continuous non-hybrid plate girders without longitudinal stiffeners, composite with a reinforced normal-density-concrete deck slab.
. There are no structural steel transverse members at deck-slab level.
. The only steel cross-sections that may be in Class 4 are the webs near internal supports.
The depth of web in compression is influenced by the ratio of non-composite to compo-site bending moment and the area of reinforcement in the slab. The Class is therefore difficult to predict until some analyses have been done.
. The deck is constructed unpropped, and all structural deck concrete is assumed to be in place before any of the members become composite.
. The formwork is structurally participating precast concrete planks. They are assumed (for simplicity here) to have the same creep and shrinkage properties as the in situ concrete of the deck.
. All joints except bearings are assumed to be continuous (clause 5.1.2).
. Bearings are ‘simple’ joints, with or without longitudinal sliding, as shown in Fig. 5.1.
Transverse sliding cannot occur.
In the charts, creep and shrinkage effects are considered only as ‘long-term’ values (t! 1). The values of all Nationally Determined Parameters, such as and factors, are assumed to be those recommended in the Notes in the Eurocodes.
The following data are assumed to be available, based on preliminary analyses and the strengths of the materials to be used, fy, fskand fck(converted from an assumed fcu):
. dimensions of the flanges and webs of the plate girders
. dimensions of the cross-sections of the concrete deck and the two supporting systems, BE and CF in Fig. 5.1(a)
. details and weight of the superimposed dead load (finishes, parapets, etc.)
. estimated areas of longitudinal slab reinforcement above internal supports.
Assumptions relevant to out-of-plane system instability are as follows. The deck transmits most of the lateral wind loading to supports A and D, with negligible restraint from the two sets of internal supports. The lateral deflections of nodes B and C influence the design of the columns, but stiffnesses are such that wind-induced system instability is not possible.
The following abbreviations are used:
. ‘EC2’ means EN 1992-1-1 and/or EN 1992-2; similarly for ‘EC3’.
. A clause in EN 1994-2 is referred to as, for example, ‘5.4.2.2’.
. Symbols gk1 and gk2 are used for characteristic dead loads on the steelwork, and on composite members, respectively. Superimposed dead load is gk3. Shrinkage is gsh.
. Characteristic imposed loads are denoted qk(traffic), wk(wind) and tk(temperature).
There is not space to list on Fig. 5.15 the combinations of actions required. The notation in the lists that follow is that each symbol, such as gk2, represents the sets of action effects (MEd, VEd, deformations, etc.) resulting from the application of the arrangement of the action gk2 that is most adverse for the action effect considered.
For the variable actions qk and wk, different arrangements govern at different cross-sections, so envelopes are required. This may apply also for tk, as several sets of temperature actions are specified.
For finding the ‘cracked’ regions of longitudinal members, it is assumed that the short-term values are critical, because creep may reduce tensile stress in concrete more than
Determine elastic properties of materials: Ea,Es (taken as Ea), Ecm, etc., from 3.1 to 3.3.
Assume a mean value t0 for permanent actions, to 5.4.2.2(3).
Determine creep coefficients ϕ(∞, t0); hence find modular ratios n0, nL,s, and nL,p for short-term, shrinkage, and permanent actions, respectively (5.4.2.2(2)).
Determine free shrinkage strain, εcs(∞, 1 day), to 3.1(3) and 5.4.2.2(4)
Stability. If no buckling mode can be envisaged, as here for the superstructure, then αcr ≥ 10 can be assumed, and global analyses can be first-order, to 5.2.1(3)
Select exposure (environmental) class(es) for concrete surfaces, to 7.1(3). Hence find minimum covers to concrete from EC2/4.4, and the locations of main tensile reinforcement in composite beams. These are required for cracked section properties
Determine shear lag effective widths for global analyses:
– for concrete flanges, at mid-span and internal supports, to 5.4.1.2 – for steel flanges, find beff for SLS and ULS, to EC3-1-5/3.1 to 3.3
Imperfections. Determine system imperfections to 5.3.2(1). Out-of-plumb of supports BE and CF are relevant for these members, but are assumed not to affect this flow chart.
For imperfections of column members, see flow chart of Fig. 6.44
Estimate distributions of longitudinal stress in steel webs at internal supports, and classify them, to 5.5. If any are in Class 4, thicken them or find effective properties to EC3-1-5/2.2
Flexural stiffnesses of cross-sections. Determine EaI1 for all uncracked composite and concrete sections, for modular ratios n0, nL,s and nL,p, using effective widths at mid-span, or at supports for cantilevers (1.5.2.11). Reinforcement may be included or omitted.
Determine EaI2 for cracked reinforced longitudinal composite sections in hogging bending, with effective widths as above (1.5.2.12 ). Represent bearings by appropriate degrees of freedom
Global analyses. Are all span ratios ≥0.6?
Use stiffnesses to 5.4.2.3(3) (‘15%’ rule) for global analyses
Do global analyses for the load cases gk1 (on the steel structure), gk2, gk3, gsh, qk, wk and tk using both short-term and long-term modular ratios for the variable actions and for gk2, gk3
and long-term for gsh. Refer to expressions (D5.9) etc., for the combinations required. (END) 5.4.2.3(2) applies. Use uncracked stiffnesses and modular ratios n0, nL,s and nL,p. Analyse for load cases: gk2, gk3, gsh. Find moment and shear envelopes for qk and tk.
Find the highest extreme-fibre tensile stresses in concrete, fct,max, for the combinations listed in expression D(5.8), with effective widths to 5.4.1.2(7)
Find regions of longitudinal members where fct,max > 2fctm, and reduce stiffnesses of these regions to EaI2
Yes No
Fig. 5.15. Flow chart for global analysis for superstructure of three-span bridge
shrinkage increases it. From clause 5.4.2.3(2), the following characteristic combinations are required for finding ‘cracked’ regions:
. with traffic leading: gk2þ gk3þ qkþ 0;wwk
. with wind leading: gk2þ gk3þ 0;qqkþ wk
. with temperature leading: gk2þ gk3þ 0;qqkþ 0;wwkþ tk (D5.8) In practice, of course, it will usually be evident which combination governs. Then, only regions in tension corresponding to that combination need be determined.
For finding the most adverse action effects for the limit state ULS (STR), all combinations include the design permanent action effects:
Gðgk1þ gk2þ gk3Þ þ gsh
using the more adverse of the long-term or short-term values. To these are added, in turn, the following combinations of variable action effects:
. with traffic leading: 1:35qkþ 1:5 0;wwk
. with wind leading: 1:35 0;qqkþ 1:5wk
. with temperature leading: 1:35 0;qqkþ 1:5ð 0;wwkþ tkÞ (D5.9) For serviceability limit states, deformation is checked for frequent combinations. The combination for crack width is for national choice, and ‘frequent’ is assumed here. These combinations all include the permanent action effects as follows, again using the more adverse of short-term and long-term values:
gk1þ gk2þ gk3þ gsh
To these are added, in turn, the following combinations of variable action effects:
. with traffic leading: 1;qqkþ 2;ttk because 2;w¼ 0
. with wind leading: 1;wwkþ 2;ttk because 2;q¼ 0
. with temperature leading: 1;ttk (D5.10)
As before, it will usually be evident, for each action effect and location, which combination governs.
Flow chart for supporting systems at internal supports
At each of points B and C in Fig. 5.1, it is assumed that the plate girders are supported on at least two bearings, mounted on a cross-head that is supported by a composite frame or by two or more composite columns, fixed at points E and F. Each bearing acts as a spherical pin. Design action effects and displacements (six per bearing) are known, for each limit state, from analyses of the superstructure.
Preliminary cross-sections for all the members have been chosen. Composite columns are assumed to be within the scope of clause 6.7.3 (doubly symmetrical, uniform, etc.). The flow chart of Fig. 5.16 is for a single composite column, and is applicable to composite columns generally. For ultimate limit states, only long-term behaviour is considered, as this usually governs.
Notes on Fig. 5.16
(1) For the elastic critical buckling force Ncr, the effective length for an unbraced column, as in Fig. 5.1(b), is at least 2L, where L is the actual length. If the foundation cannot be assumed to be ‘rigid’, its rotational stiffness should be included in an elastic critical analysis, as the effective length then exceeds 2L.
In many cases, will be much less than 2, and crwill far exceed 10. These checks can then be done approximately, by simple hand calculation. Other methods of checking if second-order global analysis is required are discussed under clause 5.2.1.
Here, it is assumed that for the transverse direction, cr>10. No assumption is made for the plane shown in Fig. 5.1. The flow chart of Fig. 5.16, which is for a single column, includes second-order system effects in this plane.
(2) Out-of-plumb of columns, a system imperfection, should be allowed for as follows.
Figure 5.17(a) shows a nominally vertical column of length L, with design action effects M, N and V from a preliminary global analysis. The top-end moment M could represent an off-centre bearing. The design out-of-plumb angle for the column, , is found from clause 5.3.2(3) of EN 1993-1-1. Notional horizontal forces N are applied, as shown in Fig. 5.17(b).
Second-order global analysis for the whole structure, including base flexibility, if any, then gives the deformations of the ends of the column and the action effects NEd, etc.,
Yes Determine elastic properties of materials, mean value t0, creep coefficients ϕ(∞, t0), modular ratios n0, nL,s and nL,p, and shrinkage strain, εcs(∞, 1 day), as in Fig. 5.15.
Select exposure class(es) for concrete, and find minimum covers, all as in Fig. 5.15.
All effective widths are assumed to be actual widths. Check that concrete covers satisfy 6.7.5.1, and reinforcement satisfies 6.7.5.2. Modify if necessary
For a concrete-encased section, find concrete cross-section for use in calculations from 6.7.3.1(2) on excessive cover. Check that 6.7.3.1(3) on longitudinal reinforcement and 6.7.3.1(4) on shape of section are satisfied
Find Npl,Rd from eq. (6.30), steel contribution ratio δ from eq. (6.38), and check that 0.2 ≤ δ ≤ 0.9, to 6.7.1(4). Find Npl,Rk to 6.7.3.3(2)
Determine Ncr and then λ, to 6.7.3.3(2). Check that λ ≤ 2, to 6.7.3.1(1). See Note 1 in main text
Estimate ratio of permanent to total design normal force (axial compression) at ULS Hence find Ec,eff from eq. (6.41), to allow for creep. Find the characteristic and design flexural stiffnesses, (EI )eff and (EI )eff,II, from eqs (6.40) and (6.42)
Note: Until the final box, below, the chart is for both y and z
Repeat for the other plane of bending. Include member imperfection only in the plane where its effect is more adverse; 6.7.3.7(1) (END) Find system imperfection φ to EC3-1-1/5.3.2(3) and hence notional transverse forces NEdφ at ends of column, and add to coexisting transverse forces (e.g. from wind loading) See Note 2 in the main text
No
Note: For verification of the column length, see flow chart of Fig. 6.44 Estimate maximum design axial force, NEd. Find αcr = Ncr/NEd. Is αcr≥ 10? See Note 1 Is αcr < 4?
Fig. 5.16. Flow chart for global analysis of a composite column
needed for verification of the column length. In Fig. 5.17(c), 0 is the rotation of the column base, and wEd represents the transverse loading, which may be negligible. For the determination of the bending moments within a column length and its verification, reference should be made to the flow chart of Fig. 6.36 of Ref. 5.
L
M
wEd
MEd,1
MEd,2
VEd,1
VEd,2
NEd
NEd
M N N
(a) (b) (c)
V + Nφ V
φ
φ0
Fig. 5.17. System imperfection and global analysis for a column