Check Operate Value/Reset Value/Oper ate Timing for all phases OK/ NOT OK Zone-I OK/ NOT OK Zone-II OK/ NOT OK Check Zone OK/ NOT OK Block Auto-reclose for all CB’s Connected Zone-I OK/ NOT OK Zone-II OK/ NOT OK ii If directional Element provided ,Relay tested & Direction found O.K OK/ NOT OK iii Test results enclosed & accepted

iv

Zone-I Tripping extended to :

Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No

v

Zone-II Tripping extended to :

Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No

vi

LBB/BFR trip checked & extended to Zone-I

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

vii

LBB/BFR trip checked & extended to Zone-II

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

viii Transfer Bus Trip Checked OK/ NOT OK

ix Close Interlock in case of BB Trip Checked for all applicable CB’s

x RESET Working properly Yes/ No

xi DC selection working properly for DC-I & II Yes/ No xii Carry out stability test by simulating external and internal faults by

primary injection and measure spill currents in Bus bar diff. relay

OK/ NOT OK

xiii Verify stabilizing resistor & Metrosil connection(wherever applicable)

OK/ NOT OK

xiv

Check for CT switching relay operation, in case of DMT scheme by closing respective isolators. Also inject current at the relay panel entry point and measure current at Bus Bar protection relay terminals after operating respective CT switching relay

OK/ NOT OK

1. Disturbance recorder

i Check communication to PC/Terminals/Printers OK/ NOT OK ii Check All Analog Inputs (residual Voltages &

R-Y-B-Neutral currents)

OK/ NOT OK iii Check Conversion( Primary to secondary ratio) settings are

programmed as per scheme

OK/ NOT OK iv Check contacts status of all digital inputs OK/ NOT OK

v

Normally six I/P’s are from Tw o CB’s. check Selective phase operation for RYB Poles for both the CB’s. Ensure proper show of Phase/Pole

OK/ NOT OK

vi Check Analog threshold setting OK/ NOT OK

vii

Check whether all digital Inputs are programmed for initiation of recording Disturbance as well as right status( NO/NC). Also check the sequence of digital channels as per Technical specifications

OK/ NOT OK

viii Run self-diagnostic program & get a print for future reference.

Otherwise, note down various Voltages at Monitoring points

OK/ NOT OK

ix Simulate a disturbance by shorting contacts of a Digital I/P. Check recording in progress. Print the same

OK/ NOT OK x Repeat the above for all digital I/P Contacts OK/ NOT OK xi

For analog threshold values (if provided), connect to Standard test kit to DR & test Threshold Value initiation of recording by Varying Voltages & Frequencies( Voltage Th reshold, Frequency thresholds

& DF/DT thresholds)

OK/ NOT OK

xii

Check Time synchronizing by altering Time Zone in TSE. Restore on confirmation. Also check time stamping in the relays by

externally triggering DR and record the error w.r.t. GPS time

OK/ NOT OK

xiii Check all analogue & digital inputs are configured as per power grid standard list

OK/ NOT OK xiv Compare/Check analog value displayed on PC with the injected

input analog value

OK/ NOT OK xv Take a print out of DR settings & ke ep for future reference OK/ NOT OK xvi Check for availability of proper software OK/ NOT OK 2. Sequential Event Recorder

i Check communication to PC/Terminals/Printers OK/ NOT OK ii Check contacts status of all digital inputs OK/ NOT OK iii Check whether all digital Inputs are programmed with right status( OK/ NOT OK

Busbar Protection

Check Operate Value/Reset Value/Oper ate Timing for all phases OK/ NOT OK Zone-I OK/ NOT OK Zone-II OK/ NOT OK Check Zone OK/ NOT OK Block Auto-reclose for all CB’s Connected Zone-I OK/ NOT OK Zone-II OK/ NOT OK ii If directional Element provided ,Relay tested & Direction found O.K OK/ NOT OK iii Test results enclosed & accepted

iv

Zone-I Tripping extended to :

Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No

v

Zone-II Tripping extended to :

Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No Trip relay Location ………… for CB No………. LBB Initiated Yes/ No PLCC/D.T. Yes/ No

vi

LBB/BFR trip checked & extended to Zone-I

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

vii

LBB/BFR trip checked & extended to Zone-II

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

From CB No………. OK/ NOT OK

viii Transfer Bus Trip Checked OK/ NOT OK

ix Close Interlock in case of BB Trip Checked for all applicable CB’s

x RESET Working properly Yes/ No

xi DC selection working properly for DC-I & II Yes/ No xii Carry out stability test by simulating external and internal faults by

primary injection and measure spill currents in Bus bar diff. relay

OK/ NOT OK

xiii Verify stabilizing resistor & Metrosil connection(wherever applicable)

OK/ NOT OK

xiv

Check for CT switching relay operation, in case of DMT scheme by closing respective isolators. Also inject current at the relay panel entry point and measure current at Bus Bar protection relay terminals after operating respective CT switching relay

OK/ NOT OK

1. Disturbance recorder

i Check communication to PC/Terminals/Printers OK/ NOT OK ii Check All Analog Inputs (residual Voltages &

R-Y-B-Neutral currents)

OK/ NOT OK iii Check Conversion( Primary to secondary ratio) settings are

programmed as per scheme

OK/ NOT OK iv Check contacts status of all digital inputs OK/ NOT OK

v

Normally six I/P’s are from Tw o CB’s. check Selective phase operation for RYB Poles for both the CB’s. Ensure proper show of Phase/Pole

OK/ NOT OK

vi Check Analog threshold setting OK/ NOT OK

vii

Check whether all digital Inputs are programmed for initiation of recording Disturbance as well as right status( NO/NC). Also check the sequence of digital channels as per Technical specifications

OK/ NOT OK

viii Run self-diagnostic program & get a print for future reference.

Otherwise, note down various Voltages at Monitoring points

OK/ NOT OK

ix Simulate a disturbance by shorting contacts of a Digital I/P. Check recording in progress. Print the same

OK/ NOT OK x Repeat the above for all digital I/P Contacts OK/ NOT OK xi

For analog threshold values (if provided), connect to Standard test kit to DR & test Threshold Value initiation of recording by Varying Voltages & Frequencies( Voltage Th reshold, Frequency thresholds

& DF/DT thresholds)

OK/ NOT OK

xii

Check Time synchronizing by altering Time Zone in TSE. Restore on confirmation. Also check time stamping in the relays by

externally triggering DR and record the error w.r.t. GPS time

OK/ NOT OK

xiii Check all analogue & digital inputs are configured as per power grid standard list

OK/ NOT OK xiv Compare/Check analog value displayed on PC with the injected

input analog value

OK/ NOT OK xv Take a print out of DR settings & ke ep for future reference OK/ NOT OK xvi Check for availability of proper software OK/ NOT OK 2. Sequential Event Recorder

i Check communication to PC/Terminals/Printers OK/ NOT OK ii Check contacts status of all digital inputs OK/ NOT OK iii Check whether all digital Inputs are programmed with right status( OK/ NOT OK

NO/NC)

iv Selective checking of each & every contacts is to be done in sequences. Print-Out/Display is to be compared

OK/ NOT OK

v

Normally six I/P’s are from Tw o CB’s. check Selective Phase operation for RYB Poles for both the CB’s. Ensure proper show of Phase/Pole.

OK/ NOT OK

vi Check Time synchronizing by altering Time Zone. Restore on confirmation

OK/ NOT OK vii Take a print out of plant status (if available) and compare with the

actual status

OK/ NOT OK

viii Check for availability of proper software & site programmability of event text

OK/ NOT OK

3. OLTC/RTCC for Transformer

i

OLTC Operation checked from

Local Panel OK/ NOT OK

Remote Panel OK/ NOT OK

Super/Control Panel OK/ NOT OK

ii Tap Position Display OK/ NOT OK

iii Correct Tap position display at local panel & at remote display with respective OLTC indicator.

OK/ NOT OK

iv All Indicating lamps checked OK/ NOT OK

v Tap Position Discrepancy Trip OK/ NOT OK

vi

Master/Follower scheme Checked for Master :Xformer-1 OK/ NOT OK Master :Xformer-2 OK/ NOT OK Master :Xformer-3 OK/ NOT OK vii Check auto supply changeover feature for OTLC/Transformer (If

available)

OK/ NOT OK

4. General

i

Many a time, different Auxiliary voltages are used for drive power of DR & EL.For example, relay DC is 220 V, DR has it’s isolated optical I/P , EL has 50 V drive DC. C onscious effort is to be put to keep all voltage contacts of relay, DR & EL isolated from each other

OK/ NOT OK

ii In case any changes are to be made in terminal designation, corresponding change in ferruling

Done/ Not done iii In each & every panel & Marshalling Boxes/Kiosks, CT & CVT

Circuits must be provided with Disconnecting stud type terminals

OK/ NOT OK

iv 20% spare TB’s provided in all types OK/ NOT OK

v

Close Interlock of CB: In case trip relay is energized, Close

command not forwarded. Normally, Manual Close command from CP must be in series with One set of NC contact of the Trip relay

OK/ NOT OK

vi

CB in OFF Condition Selective checking of Trip-CKT Supervision relay of all CB’s.by Opening wire from TC, one by One.Repeat the same with CB in On Condition

vii Permissive Tripping command thr’ PLCC Main-I Main-II 1st CH. Return Time ………. mS ………. mS

2nd CH. Return Time ………. mS ………. mS

viii If substantial difference noted in above, reason for the difference ……….

ix Any Prospect for reduction of Diff. in Time Yes/ No

x Hanging of RTU reported in Event logger Yes/ No

xi Reporting of communication failure of each channel in SER Yes/ No xii Any data error encountered during isolator operation Yes/ No xiii Suggestion for improvement………..

5. General

i Single point earthing must be ensured for CT&PT circuit Yes/ No ii In case of four CT scheme ensure summation of Main/Tie/ Reactor

CTs secondary to input of relay/ meters

Yes/ No

6. Final Documentation Review

S.No. Description Status

(Yes/ No)

Remarks (Record deficiencies, if any)

1. Final document of Pre-commissioning checks reviewed and approved

2. Documents regarding spares, equipment, factory reports, O&M manuals etc. available at site for O&M purpose

3. After modification, if any, “As built drawing are available at

site

NO/NC)

iv Selective checking of each & every contacts is to be done in sequences. Print-Out/Display is to be compared

OK/ NOT OK

v

Normally six I/P’s are from Tw o CB’s. check Selective Phase operation for RYB Poles for both the CB’s. Ensure proper show of Phase/Pole.

OK/ NOT OK

vi Check Time synchronizing by altering Time Zone. Restore on confirmation

OK/ NOT OK vii Take a print out of plant status (if available) and compare with the

actual status

OK/ NOT OK

viii Check for availability of proper software & site programmability of event text

OK/ NOT OK

3. OLTC/RTCC for Transformer

i

OLTC Operation checked from

Local Panel OK/ NOT OK

Remote Panel OK/ NOT OK

Super/Control Panel OK/ NOT OK

ii Tap Position Display OK/ NOT OK

iii Correct Tap position display at local panel & at remote display with respective OLTC indicator.

OK/ NOT OK

iv All Indicating lamps checked OK/ NOT OK

v Tap Position Discrepancy Trip OK/ NOT OK

vi

Master/Follower scheme Checked for Master :Xformer-1 OK/ NOT OK Master :Xformer-2 OK/ NOT OK Master :Xformer-3 OK/ NOT OK vii Check auto supply changeover feature for OTLC/Transformer (If

available)

OK/ NOT OK

4. General

i

Many a time, different Auxiliary voltages are used for drive power of DR & EL.For example, relay DC is 220 V, DR has it’s isolated optical I/P , EL has 50 V drive DC. C onscious effort is to be put to keep all voltage contacts of relay, DR & EL isolated from each other

OK/ NOT OK

ii In case any changes are to be made in terminal designation, corresponding change in ferruling

Done/ Not done iii In each & every panel & Marshalling Boxes/Kiosks, CT & CVT

Circuits must be provided with Disconnecting stud type terminals

OK/ NOT OK

iv 20% spare TB’s provided in all types OK/ NOT OK

v

Close Interlock of CB: In case trip relay is energized, Close

command not forwarded. Normally, Manual Close command from CP must be in series with One set of NC contact of the Trip relay

OK/ NOT OK

vi

CB in OFF Condition Selective checking of Trip-CKT Supervision relay of all CB’s.by Opening wire from TC, one by One.Repeat the same with CB in On Condition

vii Permissive Tripping command thr’ PLCC Main-I Main-II 1st CH. Return Time ………. mS ………. mS

2nd CH. Return Time ………. mS ………. mS

viii If substantial difference noted in above, reason for the difference ……….

ix Any Prospect for reduction of Diff. in Time Yes/ No

x Hanging of RTU reported in Event logger Yes/ No

xi Reporting of communication failure of each channel in SER Yes/ No xii Any data error encountered during isolator operation Yes/ No xiii Suggestion for improvement………..

5. General

i Single point earthing must be ensured for CT&PT circuit Yes/ No ii In case of four CT scheme ensure summation of Main/Tie/ Reactor

CTs secondary to input of relay/ meters

Yes/ No

6. Final Documentation Review

S.No. Description Status

(Yes/

No)

Remarks (Record deficiencies, if any)

1. Final document of Pre-commissioning checks reviewed and approved

2. Documents regarding spares, equipment, factory reports, O&M manuals etc. available at site for O&M purpose

3. After modification, if any, “As built drawing are available at

site